If the purpose of the PV system is to offset utility power consumption, then
use a battery-less PV system. I'm not saying this because John Berdner is right
(he is). I have lived with an older SW4048 inverter on my grid tie PV system
with battery backup for 4 years. The system works fine (that's installer lingo
for no callbacks).
Define your UPS needs and serve them separately. I am still a strong believer
in separating zero-time power needs (computer, security, life support, phasers,
etc.) from other needs (lights, refrigerator, well pump, TV unless something
good is on, etc.)
I don't like combustion generators automatically turning on and off. We've all
heard stories about generators running without oil, cars with auto-start warmup
in Minnesota starting up in gear and driving through the wall, etc. The test of
a good UPS is that the least technical adults (or precocious pre-teens) should
be able to turn on lights, heat, water and communications during a power outage
in the dark without hurting themselves. A few well-marked switches are
appreciated.
Switch #1 - Turn this swith on first.
Switch #2 - Turn this switch on after turning on Switch #1.
Etc.
Antony Tersol wrote:
> I have a question regarding possible configurations for a large
> residential power system. Following is description of situation and my
> analysis thus far. Any comments, feedback, experience with such a
> system, generator/inverter recommendations?
>
> Thanks, Antony
>
> We have a residential client interested in a PV system who already
> decided on having generator backup as well. They have critical loads
> that they want always provided, and power occasionally is out for days
> when trees take out the lines (they are also concerned about possible
> longer-term outages - earthquake or other disasters taking out regional
> power). It seems logical to use batteries with a generator to buffer
> the demand. If the batteries run low, the engine generator runs at full
> powerits most cost- and fuel-efficient mode of operationuntil they are
> charged. Without batteries, the generator will be running continuously
> at night even if the only load is extremely small (that blinking 12:00
> on the vcr clock that no one ever set).
>
> 1. If we go with straight grid-tie batteryless PV, we would need a
> transfer switch downstream, so that the PV wouldn't be running in outage
> situation when generator is on.
>
> grid------panel------transfer switch--------------main panel-----load
> | |
> inverter inverter
> | | |
> PV battery generator
>
>
>
> advantages: a. relative simplicity
> b. generator can power the entire main panel
> c. PV doesn't take efficiency hit from batteries
> disadvantages: a. PV useless when power is out
> b. redundant inverters?
>
> 2. If we use PV with battery, and multiple small inverters (~5kw):
>
> grid--------------main panel---------inverter-------sub panel------load
> | | |
> | battery generator
> | |
> | PV
> |
> |------------inverter-------sub panel------load
> | | |
> | battery generator
> | |
> | PV
> |
> etc.
>
> advantages: a. PV functional during outages, minimizing generator needs
> b. redundancy, so that even if one inverter fails, still have power
> c. using same inverters as likely in other smaller systems, so our
> technical knowledge better leveraged (better for us and the client)
> disadvantages: a. increased complexity - need sub-panels and need to
> feed generator into each inverter
> b. loss of efficiency because of battery losses
>
> 3. If we use PV with battery, and one large inverter (10 to 20 kw):
>
> grid--------------main panel---------inverter-------sub panel-----load
> | | |
> | battery generator
> sub panels |
> PV
>
>
> advantages: a. PV functional during outages, minimizing generator needs
>
> disadvantages: a. loss of efficiency because of battery losses
> b. no redundancy, if inverter fails, no power
> c. large inverter unique to large systems, so our experience and
> knowledge limited.
> d. only sub panel connected to inverter has backup power
>
> Parameters:
>
> House will have 400 amp service
> Typical load expected to be 40-70 amps (@ 120v), 80-100 amps max
> PV system 10-20 kwp
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list