Dave,

My experience with current transformer meters (my previous house had one) is
that most of them only read the absolute value of current and will read
reverse current flow as energy usage not energy production. That meter will
almost certainly need to be replaced.

Bill.


-----Original Message-----
From: David Palumbo, Independent Power & Light [mailto:ipl at sover.net]
Sent: Friday, May 10, 2002 7:10 AM
To: Wrenches
Subject: [RE-wrenches]


I just had a call from an electrician who has a customer interested in a
net-metered pv system.
One question he had concerned the current transformer on the 400 amp service
and if the meter will spin backwards on this
one. He says the meter is wired differently than on a system without the
current transformer. It is a single phase 240 volt supply.

Thanks,
Dave

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================








More information about the RE-wrenches mailing list