Experience with 3 Phase High Leg Delta? [RE-wrenches]

Kent Sheldon kentsheldon at sbcglobal.net
Fri Apr 26 09:00:43 PDT 2002


Matt, et al,

>This reduces the kWH production due to the transformer losses and
raises >the installation costs, offsetting any savings you may have been
counting >on related to using the Sunny-Boy versus another Hi-Volt DC,
3-Phase AC >Inverter.


No angry words to you... Remember, I used to work the 3 phase side of
the biz. One thing to watch out for: If you have any Delta (open or
closed) system with a center tapped or corner ground, you may have
grounding problems with a 3 phase inverter. You will probably need an
isolation transformer between the inverter and the grounded Delta system
because of the ground loops caused by the grounded PV array. I've seen
many inverters go boom because of this. One more reason to dump the
grounded PV requirement.

____________________________________________
Kent Sheldon
Manager, Industrial Power Systems
SMA America
ksheldon at sma-america.com
925 513 8813 Brentwood Office (Primary)
530 273 4848 Grass Valley Office

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================





More information about the RE-wrenches mailing list