Bill,
I'm glad we are continuing the dialogue on lightning. It would be good to
arrive at definitive answers to this ongoing question. In Colorado,
lightning is of major consequence, especially in mountainous areas.
At 06:45 AM 4/13/02 -0700, you wrote:
Drake,
One thing to make very clear is that the effects of most lightning occurs by
induction during a typical strike away from the energy system (direct
strikes can do whatever they feel like doing).
*************************************************************************
By "induction," I'm assuming that you mean that the lightning strike
creates a magnetic field, which as it rises and falls, creates voltage, and
therefore current in the wire. I.E., a varying magnetic field across a
wire will create current in the wire through "inductance."
There are certainly a lot of scenarios that happen when lightning
strikes. As you say, a direct lightning strike will do as it pleases. The
mega volt lightning bolt will not even "see" the 600 volt insulation on the
conductors.
Let's look at a scenario where two wires in the same conduit have
electrical potential induced into them by a lightning surge. If one
conductor is grounded, the grounding electrode will shunt the high
potential to ground. If the ground is good, the grounded conductor will
remain close to ground potential. The induced potential will be mainly in
the ungrounded conductor. Therefore, there will be a large voltage
difference between the two wires. The internal components of the system
will "see" a high voltage.
If neither of the wires are grounded, then the voltage will rise and fall
equally on both wires. Since there will be little voltage difference
between the two wires, the system components will not "see" high voltage.
How lightning protection works is controversial. It used to be believed
that lightning rods functioned mostly by conducting lightning safely to
ground. There are instances where this appears to have been the case.
The theory that seems most plausible to me, at least in most cases, is that
grounded metal in the air equalizes static potential between the atmosphere
and ground, before it reaches flash potential. Electrical potential seeks
ground. Although it is often said that lightning strikes from the ground
upward, it is still an equalizing effect.
When lightning strikes in the vicinity, substantial potential will be
conducted to ground. The more static that can be equalized in the
atmosphere in the vicinity of an installation, the less likely a close
strike will be.
But say a strike occurs a quarter mile away and an installation is exposed
to a surge, how will the energy dissipate?
If the circuit conductors are ungrounded, they will have little direct
attraction for the surge. The electrical potential will be conducted down
the frame ground. If voltage is magnetically induced into the wiring, both
ungrounded conductors will rise and fall in their potential at
approximately the same rate.
But, if one of the conductors is grounded, it could create a differential
in the wiring. If it is bonded to the metal frame, the grounded circuit
conductor will be at the same potential as the frame. The frame will be in
direct electrical connection with the charged atmosphere, with absolutely
no insulation to protect the wire from the elevated voltage.
This appears to be a major root of the present question. Does atmospheric
potential get into a system through exposed metal bonded to a circuit
conductor, or are all the effects magnetic? Hikers often report hair and
beards reacting to static before strikes. The rule is to hit the ground
immediately in these situations. Does this type of voltage get into a PV
or wind system?
I still believe that the best way to protect against lightning is to ground
the array frame to its own rod. If possible, leave all wires ungrounded,
and do not connect the array frame to any other part of the system.
If it is necessary to ground the negative wire (as it usually is), make
that single DC bonding connection at the system DC disconnect in the power
room. I realize that this may not always comply with current code.
I've had good luck "bullet proofing" systems that have experienced surge
damage, using this method. For high voltage systems, it may be more
important to provide grounding against electrocution hazards than to
provide the best lightning protection.
-Drake
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-wrenches
mailing list