Bill,
I see a possible problem with your recommended solution. The separate
structures provision also requires a separate single-point bond in each
"structure" between grounding conductor and a grounded conductor. On the
three-phase wild AC of many wind generators, what would be the grounded
conductor (the equivalent of AC neutral or DC negative)? Have I missed
something here?
Allan at Positive NRG

----- Original Message -----
From: "Bill Brooks" <billbrooks7 at earthlink.net>

> What about employing the grounding of separate structures provision in NEC
> 250-32 (2002 code)? If there is a grounded conductor, then that conductor
> should be grounded at the tower (or PV Array for PV) and at the service
> entrance with no ground wire between them and no metalic conduit. All
> ungrounded conductors must have surge protection (Phasor, Delta, voodoo).
> The main issue is that you cannot touch the tower or module frames while
> touch something connected to the house. The inverter, however, is working
> with conductors that are all referenced to the same grounding system.

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================





More information about the RE-wrenches mailing list