Jerry

>The system I mention utilizes Trace Tech industrial
>inverters.  Has anyone on the list done a Sunny Boy
>system with any amorphous pv?  Is there anything to
>watch out for that is different than crystalline
>arrays?

The Sunny Boy inverters work fine with amorphous PV. Amorphous is rather
easy to track due to the low fill factor (very gradual power curve).
Also, the Sunny Boys inverters will peak power track down to 240Vdc at
nominal 240Vac line voltage. The Trace Tech inverters will only track
down to approximately 320-330Vdc. So the SB's will allow for a deeper
voltage degradation on amorphous. Some other things to watch out for
with amorphous is the larger Voc-Vpp voltage window and the larger
temperature derating than crystalline PV.

Regards,
____________________________________________
Kent Sheldon
Manager, Industrial Power Systems
SMA America
kent.sheldon at sma-america.com
925 513 8813 Brentwood Office (Primary)
530 273 4848 Grass Valley Office

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================





More information about the RE-wrenches mailing list