DC GFCI [RE-wrenches]
Drake Chamberlin - Electrical Energy
solar at eagle-access.net
Fri Jan 11 15:30:17 PST 2002
<x-flowed>
The ground fault detector is near the batteries not the array. In the
event of a nail through a cable, shorting positive to ground, wouldn't the
circuit from the array continue to short even if the device were tripped?
Drake
At 02:58 PM 01/11/2002 -0800, you wrote:
>Travis,
>
>On a line-to-ground fault, the grounding path is removed and therefore the
>return path for the fault current is broken. Again, it doesn't solve all
>faults, just those that are more likely to happen. Historically, ground
>faults have been the source of failures of older arrays and various wiring
>mistakes.
>
>If you bolt the positive and negative together (e.g. with a metal staple
>through both--good reason never to use metal staples), the GFP may not
>detect this fault, but the inverter likely will because most inverters
>detect array shorts. If it is a battery-based system, the reverse current
>from the battery will normally trip the main breaker.
>
>Can you think of a fault that isn't covered? I'm sure there are some high
>impedance line-to-line faults that might go undetected, but they will likely
>deteriorate into one of these other faults and cause a trip. All-in-all, the
>GFP fills a major gap in detection of faults that normal overcurrent
>protection is likely to miss.
>
>Bill.
>
>
>
>-----Original Message-----
>From: Travis Creswell, Ozark Solar [mailto:ozsolar at ipa.net]
>Sent: Friday, January 11, 2002 12:33 PM
>To: RE-wrenches at topica.com
>Subject: Re: DC GFCI [RE-wrenches]
>
>
>I never did understand what it's protecting. I don't remember anything
>about a Canadian lab questioning them. That does sound an awful lot like
>what I posted, though.
>
>The main problem I saw, and still do see with them was as such;
>
>A fault happens somewhere in between the inverter and the roof mounted
>panels. The GFP detects this fault and opens the circuit. Since the
>panels are still producing power the fault is still merrily smoldering away
>on the roof or in the attic until sunset. Hopefully the customer notices
>the breaker is tripped before the house catches fire.
>
>Wow, now that's helpful a device.
>
>Travis Creswell
>Ozark Energy Services, Inc.
>----------
> >From: Drake Chamberlin - Electrical Energy <solar at eagle-access.net>
> >To: RE-wrenches at topica.com
> >Subject: DC GFCI [RE-wrenches]
> >Date: Fri, Jan 11, 2002, 1:08 PM
> >
>
> >Long ago, someone on the list mentioned that personnel in a Canadian Lab
> >felt that the DC GFCI, mounted near the batteries, for roof mounted systems
> >wasn't an effective safety device.
> >
> >Does anyone remember the reference on that?
> >
> >Thanks,
> >
> >Drake
> >
> >
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-wrenches
mailing list