DC-DC Converters [RE-wrenches]
    Brad Bassett 
    bsbassett at earthlink.net
       
    Sat May 18 21:50:59 PDT 2002
    
    
  
John, et al,
I tried putting together a DC-DC converter from components and not being 
an electronics engineer, apparently did not get it all together 
correctly (even with some assistance from the mfg.). We had some sort of 
noise interference with a Digital Solar controller so that it would not 
function properly; solution, put in a fully engineered instrument (in 
this case a Wilmore). I also tried in a different circumstance, using a 
Solar Converters DC-DC unit (48->12) and found (actually our customer 
found, after frying $18000 worth of radio equip) that when first 
supplied with power it lets through full voltage for a few milliseconds 
(20 ms if memory serves). This would probably not be a problem for more 
robust loads. Or, you might be able to get around it if you put a switch 
after the DC-DC and turned it on after firing up the DC-DC, but our 
customer's solution was to specify a fully engineered instrument. Until 
I become an electronics wiz, I'm going to stick with fully engineered 
instruments for DC-DC converters. Would you like some surplus DC-DC 
converter modules?
John Raynes wrote:
> 
> I took a quick look at some sites selling Wilmore converters.  The ones 
> I 
> saw look like full-fledged instruments, not components.  Really nice, 
> but 
> you're probably paying for a lot more product than you need.  I think we 
> 
> can dig up some better options among fully UL-listed components.  Most 
> will 
> need to be part of some larger system enclosure,  preferably metal for 
> heat 
> sinking. And they'll need their own fusing and/or disconnect.  But that 
> shouldn't be a problem if it's designed in to a system.
> 
> Regards,
> 
> John Raynes
> Principal Engineer
> Raynes Engineering, Inc./RE Solar
> Sandy, UT
> 
> 
> 
Brad Bassett
Schott Applied Power 
Tumwater, WA office
bsbassett at earthlink.net
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
    
    
More information about the RE-wrenches
mailing list