series circuits for Sunny Boy [RE-wrenches]
Jeffrey Wolfe, Global Resources
global at sover.net
Mon Dec 3 23:21:04 PST 2001
Bill,
Thanks for pointing that out. I'd much rather do it that way, but had not
gotten my brain there yet. Open grounded neutrals really bother me.
Jeff
On Monday, December 03, 2001 12:44 PM, Bill Brooks
[SMTP:billbrooks7 at earthlink.net] wrote:
> Jeff and others,
>
> On negative grounded arrays, it may be preferrable to break the positive
> twice (on the two outside poles) and not switch the negative. The impact
on
> the switch is the same.
>
> Bill.
>
>
> > -----Original Message-----
> > From: Jeffrey Wolfe, Global Resources [mailto:global at sover.net]
> > Sent: Sunday, December 02, 2001 9:48 PM
> > To: 'RE-wrenches at topica.com'
> > Subject: RE: series circuits for Sunny Boy [RE-wrenches]
> >
> >
> > Travis,
> >
> > One fine print note on using some of the SqD disconnects. The 600VDC
> > rating on some of them depends upon breaking BOTH the hot and the
> > negative,
> > using the outside poles of a three phase unit. The only unit I see in
my
> > Grainger book that avoids this requirement is the 200A 4-wire
> > switch, (but
> > it's not really clear it's listed for DC, and the Square D
> > catalog does not
> > rate it for DC>)
> >
> > So you're into either multiple switches or ignoring the rating.
> > The rating
> > is *probably* made in consideration of breaking the DC under load at a
> > level of 200A, but still and all, that's the rating.
> >
> > I'd stick with the combiner box.
> >
> > Jeff
> >
> > On Sunday, December 02, 2001 6:53 PM, Travis Creswell, Ozark Solar
> > [SMTP:ozsolar at ipa.net] wrote:
> > > Check out page 458 of the Grainger No. 392 catalog. You'll
> > have to buy a
> > 3
> > > phase model and that will give you 3 sub arrays. You can get a Nema
3R
> > > Rainproof ST/3P 600 VDC fusible disconnect (30 amp, Square D flavor)
for
> > > $401.75.
> > >
> > > Does the Trace Tech model have a handle or do you have to open the
box
> > and
> > > remove the fuses.
> > >
> > > And be ever so careful about trying to "educate inspectors". Do want
he
> > > wants on this job with a big smile on your face then carefully
> > challenge
> > him
> > > next time. Tell him how smart he is and thank him (for making life
> > > difficult) and your life will be so much easier next time. They are
the
> > > final authority so if they feel like it they can make your life very
> > > difficult.
> > >
> > > Travis Creswell
> > > Ozark Solar
> > > ----------
> > > From: "Mangelsdorf, Marco" <mmangelsdorf at hei.com>
> > > To: RE-wrenches at topica.com
> > > Subject: series circuits for Sunny Boy [RE-wrenches]
> > > Date: Sun, Dec 2, 2001, 5:14 PM
> > >
> > >
> > >
> > > Aloha Wrenches,
> > >
> > > Does anyone know of a relatively low cost high voltage (up to 600
VDC)
> > > combiner box that has, say, two or three fuse holders?
> > >
> > > We've finished the first Sunny Boy 2500U installation here in
> > the islands
> > > with two parallel series-wired sets of (10) BP 150-watt 24 VDC
modules.
> > > According to a reasonable interpretation of the NEC 690-9 (b), there
is
> > no
> > > need for fuse protection of each series circuit of modules. So, in
the
> > > install, I have both sets of modules wired directly to a single pair
of
> > > #10CU conductors with no fuses. The inspection did not pass last
friday
> > > with the notation being that there was no overcurrent protection on
the
> > > roof, i.e., no combiner box with separate fuses to protect each
series
> > > string. I'm going to try and educate our local authorities tomorrow
on
> > the
> > > lack of need for fuses on the roof with a cover letter of my own and
a
> > > two-page letter that John Berdner of SMA-America has been kind enough
to
> > > supply me with. BUT....in case I don't prevail in my education
> > process,
> > I'm
> > > looking for a low cost plan B. I know that I can get a 10-circuit
> > combiner
> > > from Trace Tech. that's rated at the high DC voltage. But I'd like
to
> > avoid
> > > spending $400 or more bucks for it.
> > >
> > > Any ideas?
> > >
> > > thanks,
> > > marco
> > >
> > > Marco Mangelsdorf, Ph.D.
> > > Marketing and Sales
> > > ProVision Technologies, Inc.
> > > 69 Railroad Avenue, Suite A-7
> > > Hilo, Hawaii 96720 USA
> > > (808) 969-3281, fax 934-7462
> > > www.provisiontechnologies.com - - - -
> > > To send a message: RE-wrenches at topica.com
> > >
> > > Archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
> > > <http://www.topica.com/lists/RE-wrenches/>
> > >
> > > List rules etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> > > <http://www.mrsharkey.com/wrenches/etiquete.htm>
> > >
> > > Check out participant bios: www.mrsharkey.com/wrenches/index.html
> > >
> > > Hosted by Home Power magazine
> > >
> > > Moderator: michael.welch at homepower.com
> > >
> > > - - - -
> > > To send a message: RE-wrenches at topica.com
> > >
> > > Archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
> > >
> > > List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
> > >
> > > Check out participant bios: www.mrsharkey.com/wrenches/index.html
> > >
> > > Hosted by Home Power magazine
> > >
> > > Moderator: michael.welch at homepower.com
> > >
> > > << File: ATT00001.htm >>
> >
> > - - - -
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> >
> > List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> >
> > Check out participant bios: www.mrsharkey.com/wrenches/index.html
> >
> > Hosted by Home Power magazine
> >
> > Moderator: michael.welch at homepower.com
> >
> >
> >
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list