I asked an inspector before doing exactly the same thing. He quoted the
CEC (Canadian Electrical Code) which states:
Rule 10-906 (3) - The bonding conductor shall be secured to every metal
box by means of a bonding screw, which shall be used for no other
purpose.
His interpretation was that this precludes using the mounting bolts as
bonding method. I don't know what the NEC says, but, as in tax law,
interpretation is the name of the game.
>If the module array rack is metal, when bolting the modules to the rack
you
>can use star washers between the module frame and the rack, tightening
well
>to assure the washers bite into both surfaces. Then just ground the
array
>rack itself. Codeman John Wiles told me years ago this is legal. If a
module
>is removed, the other module frames will still be grounded through
their
>respective star washers.
----------------------------------------------------------------------
Eric Smiley
Project Leader - BCIT Technology Centre
NE25-3700 Willingdon Ave. Burnaby, BC V5G 3H2
ph: (604)432-8657 esmiley at bcit.ca www.tc.bcit.ca
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list