Dual SW battery charging [RE-wrenches]
Clive Wilkins, PowerSense
powersense at horizon.co.fk
Thu Sep 27 14:51:35 PDT 2001
Hi Chuck,
I have parallel-stacked SW4548 E `s and always use the slave inverter to
control auto gen start.
The following might help but I haven't series-stacked so someone else might
want to comment:
Menu 11 AC INPUTS:
Set input lower
Set master at least 5v ac lower than slave (for 120v systems)
Set INPUT UPPER AC LIMIT - master should be at least 5v ac higher than
slave.
Menu 13 GEN STARTING DETAILS - set the generator warm-up seconds:
Master 40 secs.
Slave 60 secs.
Menu heading 10 BATTERY CHARGING -
set absorption time on master to a longer setting, say 15 minutes, than the
slave.
With parallel stacking, the AC neutral terminals are connected together at
the inverters.
I also connect the DC neg. at the inverter terminals.
Hope this helps. A good guy to call at Trace/Xantrex is Steve Higgins at
ext. 2226, he has helped me out in the past.
cheers
Clive
Clive Wilkinson
PowerSense
Dunnose Head Farm
Falkland Islands
tel +500 42202
fax +500 42203
powersense at horizon.co.fk
http://www.falklandwool.com/power
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list