AFI breakers [RE-wrenches]
Drake Chamberlin - Electrical Energy
solar at eagle-access.net
Tue Aug 14 17:49:08 PDT 2001
<x-flowed>
Also, the NEC only will require them in bedrooms of dwelling units.
.
210-12. Arc-Fault Circuit-Interrupter Protection
(a) Definition. An arc-fault circuit interrupter is a device intended to
provide protection from the effects of arc faults by recognizing
characteristics unique to arcing and by functioning to de-energize the
circuit when an arc fault is detected.
(b) Dwelling Unit Bedrooms. All branch circuits that supply 125-volt,
single-phase, 15- and 20-ampere receptacle outlets installed in dwelling
unit bedrooms shall be protected by an arc-fault circuit interrupter(s).
This requirement shall become effective January 1, 2002.
At 06:18 PM 08/14/2001 -0600, you wrote:
>The NEC has them become a requirement as of Jan. 1, 2002.
>
>Drake
>
>At 06:42 PM 08/14/2001 -0400, you wrote:
>
>>Hello,
>>
>>I was working at a job site today with a licensed electrician. He showed
>>me a few SQD AFI (arc fault interrupt) breakers he was installing in the
>>load center. They will trip if an arc is detected, such when plugging an
>>appliance (w/ its on board power switch on) into a live outlet. He said
>>they are now required for any cicuit in a "habitable" room. Comments,
>>please?
>>
>>Kirk
>>
>>
>>--
>>Vermont Solar Engineering - a Trace Certified Dealer
>>Kirk Herander
>>PO Box 697
>>Burlington, VT. 05402
>>800.286.1252 - 802.863.1202
>>fax 802.863.7908
>>
>>- - - -
>>To send a message: RE-wrenches at topica.com
>>
>>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>>
>>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>>
>>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>>
>>Hosted by Home Power magazine
>>
>>Moderator: michael.welch at homepower.com
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-wrenches
mailing list