Grid Tie 240 VAC w/ transfer switch? [RE-wrenches]
Jeff Clearwater
clrwater at earthlink.net
Wed Aug 8 21:49:42 PDT 2001
<x-flowed>
Hi Chris,
I would recommend a yet different approach. On a dual SW5548 system
(120/240 Volt) that I did at Sirius Ecovillage that fed 2 main
apartment panels (each 125 A Subpanels with 16 breakers each plus a
few 240 volt loads), I installed 4 GENTRANS, 2 on each panel.
That way the customer has the best of both worlds and you don't have
to rewire the whole panel or create a new critical loads sub. Every
breaker in the house can easily be put on the Traces or all can go to
the utility or any combination in between. The 4 Gentrans cost me
$800 wholesale and installation is a snap.
I use the hardwire GENTRANS - model number 30408 that has 6 15 amp
circuits and 2 20 amp or you can combine two for a 240 volt load with
6 singles left. http://nbmc.com/gentran/30408.html (I believe
GENTRAN is now offering all 20 amp circuits or at least you can
request that)
In fact I use this scheme for all my SW based intertie installations
now. It gives the ultimate transfer switch distribution flexibility
for the lowest cost and installation time and can be used on
retrofits or new construction equally well. If you have a generator
running into your Trace's then you also get to use the full 60 amp
pass throughs and power the whole house with the gen/solar in gen
support mode quite easily.
For intertie systems that insist on being in off-grid mode for the
solar loads, this system all also allows the user to fine tune the
loads so that the incoming matches the outgoing without much cycling.
I could always keep my batteries at between 60-90% by just watching
the Tri-metric and adding or subracting a circuit or two as needed
just with a throw of a switch.
If you do follow this approach make sure your grounding system is
thorough and you size your neutrals right so you don't get neutral
current on the grounds. Also make sure to provide a 30 Amp input
breaker for each GENTRAN. This system works especially well for dual
SW 120/240 volt systems.
Cheers, Hope that helps!
Jeff Clearwater
Ecovillage Design
>Dear Wrenches:
>
>My client's system is in California; he has two Bergey XL 1's on order, and
>has two Trace SW4024's and six 120W modules. He is in a place with rolling
>power outages and wants back-up (vis a vis eight of the Surrette S460
>batteries). His power is rarely out for more than an hour at a time. His
>site offers excellent sun and winds, with 15 to 18 mph averages.
>
>But, he doesn't want a separate sub-panel for his important loads. Has
>anyone done a grid-tie with a transfer switch (located before the main
>electrical service panel), where one side of the transfer switch is from
>utility power, and the other leg is 240VAC from the inverter's output? My
>client wants total back up not just dedicated loads, and says he'll "power
>down" in the event of a power failure (and yes, I've cautioned him that if
>the grid fails, it would be easy to max out his inverters). There is no
>fuel generator integrated into this system.
>
>I've talked with a nice fellow from Asco (http://www.asco.com) about
>whether their transfer switches would work for this application. We both
>think it would--but know of no one who's tested or tried this.
>
>One thing I'm uncertain about, code-wise, is feeding the utility input into
>the AC 1 "in", from the utility side of the transfer switch (like, with a
>separate 60A circuit breaker).
>
>Anybody got any ideas or experience with this type of system? I'd
>appreciate any advice you could offer.
>
>Chris Daum
>Oasis Montana Inc.
>406-777-4321 or 4309
>406-777-2632 fax
>http://www.oasismontana.com
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
--
~~~~~~~~~~~~~~~~~~~
Jeff Clearwater
Ecovillage Design Associates
780 Poplar Ave
Boulder, CO 80304
Community and Village Scale Renewable Energy Systems
303-546-0460, jeffc at ecovillage.org, clrwater at earthlink.com
Council Member - Ecovillage Network of the Americas
http://www.gaia.org/secretariats/ena/
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-wrenches
mailing list