sw5548 in sell back mode [RE-wrenches]
Kirk Herander
kirk at vtsolar.com
Fri Nov 16 14:54:31 PST 2001
Thanks. I was initially concerned that inverter #1 had a problem that would
never allow it to sell, but since figured out that they can be somewhat
balanced if bulk charge(ie sell) voltages are staggered by several vdc.
Still seems odd, though.
-----Original Message-----
From: Bill Brooks <billbrooks7 at earthlink.net>
To: RE-wrenches at topica.com <RE-wrenches at topica.com>
Date: Friday, November 16, 2001 11:28 AM
Subject: RE: sw5548 in sell back mode [RE-wrenches]
>Kirk,
>
>Aren't dual SWs fun. Welcome to balancing hell. There was a thread on this
a
>few months ago. I'll try to dig something up for you.
>
>Bill.
>
>
>> -----Original Message-----
>> From: Kirk Herander [mailto:kirk at vtsolar.com]
>> Sent: Thursday, November 15, 2001 5:27 AM
>> To: RE-wrenches at topica.com
>> Subject: sw5548 in sell back mode [RE-wrenches]
>>
>>
>> Hi folks,
>>
>> I have a dual SW5548 power panel programmed for sell back. Both inverters
>> are programmed identically -
>> bulk & float set to 52.0 volts, absorption time 0 hours, max sell amps
30,
>> max charge current 30.0 amp.
>>
>> The system includes a 5 kw array. I assummed that both inverters
>> would sell
>> power back equally, but I am witnessing an imbalance.
>> During a partially sunny day, with the batteries at the sell voltage,
>> Inverter #1 was showing a positive 1 - 3 amps on AC input, while
>> inverter #2
>> was showing -13 amps being sold back. In addition, when the PV is
>> turned off
>> and the batteries are floating at 52.0 volts, inverter #1 is
>> reading +5 amps
>> on AC input, inverter #2 reading -4 amps. I'd think that charge rate at
>> float would be balanced also, but no. The inverters' outputs are not
>> connected to any AC loads during these observations. Any ideas?
>>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list