Lightning Arrestors [RE-wrenches]

Drake Chamberlin - Electrical Energy solar at eagle-access.net
Sun Aug 12 12:24:45 PDT 2001


<x-flowed>
At 04:34 PM 08/11/2001 -0700, you wrote:
>List members,
>
>Doug Pratt wrote:
>
> > 3. Multiple ground rods in a single system are fine, but they MUST all 
> be connected
> > together.  If those connections are bare #8 wire in direct contact with 
> the ground
> > (not in conduit), then it's even easier for the lightning energy to 
> dissipate.
> >   So put in a ground rod at your PV array, put in a ground rod at the 
> base of your
> > wind tower, AND at each guy wire anchor, but HOOK THEM ALL TOGETHER 
> with buried
> > wire!
>
>Sometimes this is not practical when running long 150+' runs in from the 
>PV/ wind
>gennys. Are you saying you want 150' of #8 or #4 bare copper in the trench 
>with the RE
>delivery wires?


In this situation, the rods do not need to be bonded together in this 
way.   The locations are separate.  In the wiring for buildings, a ground 
rod is bonded to the neutral at the disconnect for the separate 
structure.  A separate conductor connecting the rods would create a 
parallel neutral path.

Drake

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




</x-flowed>



More information about the RE-wrenches mailing list