Thanks for the input Bill, one thing about our combiner boxes. We only 
have 10 and 12 circuit models now, each with or without diodes. I don't 
sell too many with diodes. They are in NEMA3R wall mount enclosures and 
are all UL1741 listed.

The 6, 12, and 22 circuit models were designs we bought from Pulse. 
These designs were pretty much off the shelf parts (fuse holders, bus 
bar, terminal blocks) manually wired together. This design worked fine 
for all the applications I provided them for. Frankly, I prefer the 
integrated bus board approach. The fewer mechanincal wire connections 
the better. I'm sure that we have all seen mechanicall connections that 
loosen over time. They become maintenance items, which seldom get 
maintenanced. There is also the cost issue. The bus board approach is 
quite a bit less expensive. I'm not sure if the Pulse designs are still 
available, given the state of Pulse. John Berdner may be able to expand 
on this.

Kent Sheldon
Product Manager, Photovoltaic Systems
Xantrex Technologies, Distributed Industrial & Utility Markets


-----Original Message-----
From: Bill Brooks <billbrooks7 at earthlink.net>
Date: Mon, 11 Jun 2001 21:38:17 -0700
Subject: RE: Outboard equipment for PV5 [RE-wrenches]

> William,
> 
> Trace Tech normally sells their equipment to companies that do their
> own
> design engineering or hire engineers to design their systems for
> them. Now
> that they offer smaller inverters, it may seem like they should
> provide more
> design input, but they are not currently setup to do this. Remember,
> they
> service a major part of the variable speed wind turbine industry with
> inverters--huge inverters.
> 
> A couple of quick tips for free--then we start charging:
> 
> 1. The Trace Tech inverter must have a floating output--either
> connected to
> a delta-delta connection or a delta-open wye configuration. This is
> an
> isolation tranformer. The only way you could use a tranformer on site
> would
> be if it was dedicated to your unit, the transformer was ungrounded,
> and is
> properly rated for the inverter. If you ground the isolation
> transformer,
> the inverter will not work. It is only grounded on the DC side
> (negative
> pole or center-tapped neu. The AC neutral is referenced to ground at
> the
> main sub panel. It is preferable to buy the transformer through Trace
> Tech.
> 
> 2. The combiner must be a 600V combiner. This is NOT a TCB-10. Trace
> sells a
> 6,12, and 22-string combiner.
> 
> 3. If the AC circuit breaker is within view of the inverter, it could
> be
> used as the AC disconnect. It would need to be at least a three-pole,
> 20-amp
> breaker.
> 
> 4. If you support the conduit properly, Rigid Non-Metallic PVC should
> be
> okay. Local codes may govern. Occasionally you run into situation
> where
> Rigid Metallic is necessary. Check with the jurisdiction first.
> 
> Bill.
> 
> 
> > -----Original Message-----
> > From: William Miller [mailto:wrmiller at slonet.org]
> > Sent: Monday, June 11, 2001 6:21 PM
> > To: RE-wrenches at topica.com
> > Subject: Outboard equipment for PV5 [RE-wrenches]
> >
> >
> > Pals:
> >
> > As you all know by now, I am bidding on installation of a Trace
> Technology
> > PV5 and I can't get Trace Tec to return my calls.  Maybe one of you
> can
> > answer some questions:
> >
> > This system will go into a facility with a 440V feeder.  There is
> an
> > existing 208 transformer and sub-panel. Trace lists some equipment
> as
> > optional and a transformer as "required" if the local building
> department
> > requires the panels be grounded or if the line voltage is not 208. 
> There
> > is no manual for the PV5.  The manual or the PV10 (AKA the 10208)
> says the
> > transformer is required, period.  The client has a 440 to 208
> transformer
> > already.  Do we still need to purchase one from Trace Tec?  By
> > grounded, do
> > they mean one pole of the DC feed or do they mean the frame of the
> panels?
> >
> > Also, they list a number of optional items and I need to know if
> > I need any
> > or all of them and how they are installed.  For example, they offer
> a 20 A
> > AC circuit breaker.  I have space for a 3 pole breaker in the 208
> panel.
> > Do I need another one?
> >
> > They list a combiner box.   This looks like the same one that has
> flamed
> > out for several wrenches.   This unit will be run at close to 600
> VDC.
> > Will it take this voltage?
> >
> > This is a code question:  This equipment will be installed at a
> public
> > pool.   Can the conduit be installed at about 8 feet above the deck
> (PVC
> > Sked 40)?
> >
> > Thanks for considering these questions.
> >
> > William Miller
> >
> >
> > __________________________________________________________________
> > William Miller
> > SLO Communications: Communications and Power Systems Consulting
> > PO Box 50, Santa Margarita, CA 93453
> > Voice :805-438-5600		Fax: 805-438-4607	VMail: 805-546-
4875
> > email: wrmiller at slonet.org
> > License No. C-10-773985
> > _____________________________________________________________
> > Compatibility:
> > Word processor: WP7
> > Spreadsheet: Quatro Pro 7
> > CAD: Microstation 95, DXF, Visio 4.1T
> > _____________________________________________________________
> > "I stand by all the misstatements that I've made." Dan Quayle
> > __________________________________________________________________
> >
> > - - - -
> > To send a message: RE-wrenches at topica.com
> >
> > Archive of previous messages:
> http://www.topica.com/lists/RE-wrenches/
> >
> > List rules & etiquette:
> http://www.mrsharkey.com/wrenches/etiquete.htm
> >
> > Check out participant bios: www.mrsharkey.com/wrenches/index.html
> >
> > Hosted by Home Power magazine
> >
> > Moderator: michael.welch at homepower.com
> >
> >
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages:
> http://www.topica.com/lists/RE-wrenches/
> 
> List rules & etiquette:
> http://www.mrsharkey.com/wrenches/etiquete.htm
> 
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
> 
> 


- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================




More information about the RE-wrenches mailing list