olar Boost / C40 test [RE-wrenches]
Allan Sindelar, Positive Energy, Inc.
allan at positiveenergysolar.com
Fri May 4 14:55:58 PDT 2001
Blair,
A PV input voltage of 28.5 is low enough to suggest that one or more of
these may apply:
* An extremely hot day and module temperature
* Excessive input voltage drop
* MPPT adjustment on the SB50 not set optimally.
I would expect to see an input voltage of around 35 volts before temperature
deration. Any ideas?
Allan at Pos Energy
----- Original Message -----
From: "blair Tump may" <tump at midcoast.com>
> Site; N44* W 069* temp amb; 92.2* panel top temp;117* back of panel
> 124.2* array ang;44* facing;185* M Elv;170'
> System SW 4024 * 375 surrette batts.15 585 panels & 1 590 panel wired
24vt DC
>
> C40' Battery voltage;25.46 panel voltage 26.32 DC amps in 39.5-40 AC
> amps to grid 7.62 Brand WT Mtr 930 Avg
>
> Solar Boost 50; Batt.Vt.25.46 Panel Vt.28.5 DC Amps in 40.9-41.2 AC Amps
> into grid 8.1 Brand WT Mtr; 970 Avg
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================
More information about the RE-wrenches
mailing list