Sq D as combiner box [RE-wrenches]
Bill Brooks
billbrooks7 at earthlink.net
Wed Apr 4 10:42:22 PDT 2001
Wrenches,
There was a fairly thorough discussion of this topic a month ago. Jack West
and others confirmed that the Heinemann breakers have a 25,000 AIR at 60
Volts--our battery bus voltage. I believe that satisfied the requirement for
current limitation.
However, as we discussed last month, I do not believe that a QO load center
is appropriate for use as a combiner box to meet the NEC. The snap-in
variety do not meet the requirement to have a fastener on all back-fed
breakers. Some inspectors allow the cover to satisfy the fastener
requirement, but not all.
Bill.
> -----Original Message-----
> From: David Palumbo, Independent Power & Light [mailto:ipl at sover.net]
> Sent: Wednesday, April 04, 2001 10:24 AM
> To: RE-wrenches at topica.com
> Subject: RE: Sq D as combiner box [RE-wrenches]
>
>
>
>
>
>
> >the Heineman breaker will not provide the AIC that
> >the QO needs--you must use a current limiting fuse.
>
> <True. There are no current limiting breakers, so a fuse is the only
> option.>
>
>
> Eric,
>
> What about the hundreds of systems out there using Trace DC250 disconnects
> (Heinemann breakers) with no current limiting fuse.
> I always used to use Class RK5, or Class T fuses until Trace came out with
> their disconnect box using the dc rated Heinemann breaker. They said that
> these breakers met code and that we no longer needed current
> limiting fuses.
>
> Dave Palumbo
>
>
> - - -
> To send a message:
> RE-wrenches at topica.com
>
> Archive of previous messages:
> http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette:
> http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios:
> www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator:
> michael.welch at homepower.com
>
>
- - -
To send a message:
RE-wrenches at topica.com
Archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator:
michael.welch at homepower.com
==^================================================================
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email To: RE-wrenches-unsubscribe at topica.com
This email was sent to: michael.welch at homepower.com
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
==^================================================================
More information about the RE-wrenches
mailing list