<x-flowed>At 11:53 AM 03/10/2001 -0800, you wrote:
>There are all sorts of faults which could develop.
>
>At 10:12 am -0800 10/3/01, Drake Chamberlin - Electrical Energy wrote:
>>
>>The code requires overcurrent protection in ungrounded conductors.
>
>As I understand it, this is because there could be a fault earth circuit
>back to the other pole behind the breaker (and this would not already have
>blown a fuse/tripped a breaker, because the system is floating).
Both wires carry electrical potential relative to each other. The two
circuit wires are just two energized, ungrounded conductors with an
unspecified relationship to ground. If the system is ungrounded, neither
wire would be grounded (or earth).
If the positive wire were to accidentally become grounded, then there would
be a negative potential relative to ground on the other wire. It would
become like the positive ground on an old auto or tractor.
With ungrounded systems, one conductor accidentally coming in contact with
ground wouldn't blow the breaker. It would take both wires touching either
ground or each other. A 2 pole breaker wouldn't solve the problem, either.
>>The resistance varies with the length of the run. It doesn't take a very
>>long run of #12 wire to limit the surge of low voltage current to well
>>within the bounds of the 5000 DC amp interrupt capability of the QO breaker.
>
>Hmm but who is to say where the fault is going to happen - which end of
>the wire? Or right at the breaker?
That is a good point. If the fault happened next to the breaker, it might
not trip This could be a problem, especially if a short occurred directly
in the breaker box. If the short happened a couple of feet away from the
box in a run of 2 wire, #12 cable, the 5000 amp limit should not be exceeded.
>>ARTICLE 720 -- Circuits and Equipment Operating at Less than 50 Volts
>>
>>720-4. Conductors
>>Conductors shall not be smaller than No. 12 copper or equivalent.
>
>that's a bit fascist. What about circuits with 1 amp fuses?
This can be a bit of a grey area, but wires that are strictly control wires
can be smaller and have a small fuse to protect them. The number 12 rule
is for wires that supply a load.
Where I've seen this get into grey areas are with El Sid pumps for DC
pumped, hot water heating. The pumps pull an amount of current that is
consistent with the amount of power pulled by control circuits. Yet they
are actual loads.
Many installers use thermostat wire fused at very low amperage for this
purpose. It is not code, but it works so long as the run is not too long
or not too many pumps are on one wire.
Drake
>Hugh
>
>Scoraig, Scotland
>http://www.scoraigwind.co.uk
>
>- - - - - - -
>To send a message:
>RE-wrenches at topica.com
>
>The archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette:
>http://www.mrsharkey.com/wrenches/etiquete.htm
>
>To unsubscribe send a message to: RE-wrenches-unsubscribe at topica.com
>
>To check out the other RE-Wrench participants:
>www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine: www.homepower.com
>
>For info contact list moderator by email:
>michael.welch at homepower.com
>
>____________________________________________________________
>T O P I C A -- Learn More. Surf Less. Newsletters, Tips and Discussions
>on Topics You Choose.
>http://www.topica.com/partner/tag01
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
</x-flowed>
More information about the RE-wrenches
mailing list