Battery sizing for running the SW [RE-wrenches]
Windy Dankoff, Dankoff Solar
windy at dankoffsolar.com
Sat Feb 24 14:44:49 PST 2001
<x-flowed>>Hey Carl all you need 4 a grid intertie is the smallest battery bank
>you can install. For a 48 vt system 4group 24 car batteries will
>work. ....
I'm baffled. Wouldn't the owner desire and also expect that there
would be some backup capability? I can't imagine not encouraging at
least a little more storage, for such a slight extra cost. In fact, a
bank that's too small may not even be able to hold up voltage under
motor-starting conditions.
Windy
- - - - - - -