Heat redistribution/timer [RE-wrenches]
Allan Sindelar, Positive Energy, Inc.
allan at positivenergy.com
Wed Feb 21 14:36:18 PST 2001
Gary,
The problem I see is 24 cycles/day on a DC-powered timer; it's probably a
custom unit. I did a similar approach recently with an AC well pump, but I
only needed 2 cycles/day. AEE sells a 12V/24V DC analog timer, part
#52-520-016 ($90 retail) to control the relay. Their catalog suggest a
minimal on or off cycle of 15 minutes, using trippers to activate a switch.
As extra trippers can be added, in theory you could do 48 cycles/day...but
the switch might wear out in a few years, and it's pretty spendy...
If you use a T240, make sure that the relay controls the input side, to
avoid phantom loads. Also use a DC coil relay, for same reason. But
hey--if the motor is only 1/3 hP, it's probably reconnectable as 120VAC.
Have you checked that out?
Allan at Pos E
----- Original Message -----
From: "Gary Higbee, Solutions from the Land" <ghigbee at efn.org>
Subject: Heat redistribution/timer [RE-wrenches]
> I'm working with a client who would like to be able to run his 1/3hp
> 240-volt circulating fan.
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
List rules & etiquette:
http://www.mrsharkey.com/wrenches/etiquete.htm
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
____________________________________________________________
T O P I C A -- Learn More. Surf Less.
Newsletters, Tips and Discussions on Topics You Choose.
http://www.topica.com/partner/tag01
More information about the RE-wrenches
mailing list