Trace reply: Charger drops offline [RE-wrenches]
Chuck Heath, SunPower
sunpwr at jps.net
Thu Aug 10 14:45:40 PDT 2000
Here's the reply I received from Trace tech support. I won't have a
chance to try their suggestions for a few days, but will report back
after I do.
Thanks to all wrenches who offered help and suggestions.
Cordially, Chuck
-=-=-
Chuck,
Put gen input to AC1, select "off" in gen menu and manually start
generator.
If results are the same, the there is a problem with the generator voltage
or frequency. Rarely do both AC1 and AC2 fail at the same time. We can
take
a look at the inverter here to be sure but if no problems are found, there
will be a $60. bench fee.
Bryan A. Dybvig
Xantrex Trace Engineering
Product Support Technician
bdybvig at traceengineering.com
(360) 435-8826 EXT. 2203
> -----Original Message-----
> From: Chuck Heath [SMTP:sunpwr at jps.net]
> Sent: Monday, August 07, 2000 11:20 AM
> To: Bryan
> Subject: Charger drops offline
>
> This is a repeat of the email sent 7/12/00 for which I'm still seeking
> answers, or an RMA to return the unit. Please confirm receipt of this
> message, since Bryan left a telephone message saying he never received
> the original email message.
>
> Client reported charger of a SW 4024 (v. 4.01, s/n W4649) not working
> properly. Site visit confirmed this. Only charging source is a
> propane-fueled Kohler 12 RY generator, re-wired for 120 VAC (12 kW before
> altitude derating). Battery is type 85-25 two-volt cells, 1270 AH @ 20
> hr. discharge rate. System installed in February, 1997.
>
> Symptoms: Trace sees AC-2 Good from Kohler, goes into Bulk charging for
> only 30-35 seconds, then drops out of Bulk and back to inverting for 10
> seconds until cycle repeats. Kohler voltage is a steady 117-118 VAC
> whether under load or not. Trace reports Kohler frequency as rock-solid
> 60 cps.
>
> After nearly 6 hours generator runtime, was able to raise battery voltage
> from 26.8 to 27.2 VDC - not nearly enough. At-rest battery voltage was
> 24.9 VDC. Set Gen Amps AC (Menu #11) and Set Max Charge Amps AC (Menu
> #10) are both at 35 Amps AC. Lower values did not change results, nor did
> changing Set Float Voltage (27.1 VDC) to match Set Bulk Voltage setting
> (Menu #10) of 29.8 VDC. Inverter/Charger AC Amps while charging was 30-32
- - - - - - -
To send a message:
RE-wrenches at topica.com
The archive of previous messages:
http://www.topica.com/lists/RE-wrenches/
To unsubscribe send a message to:
RE-wrenches-unsubscribe at topica.com
To check out the other RE-Wrench participants:
www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine:
www.homepower.com
For info contact list moderator by email:
michael.welch at homepower.com
___________________________________________________________
T O P I C A The Email You Want. http://www.topica.com/t/16
Newsletters, Tips and Discussions on Your Favorite Topics
More information about the RE-wrenches
mailing list