Found my old "Pocket Reference"
It says
231 Cu. Inches per US liquid gallon
.13368 Cu. Ft pr liquid gallon
kW = 3409.5 BTU's
1 HP = .746 kW
Horsepower hour = ~2550 Btu's
So a 16 hp motor is going need around 40,800 BTU's/hour ???
If we add in a 30% eff factor for Internal Combustion engines that takes us
to a more realistic 136,000 Btu's hr.
My local propane supplier tells me @60F
91,690 BTU's per gallon of propane
21,591 BTU's/lb
2,516 BTU's Cu. Ft
A 16 hp motor will produce 12.3 kW (16x.746). Although I have seen several
20 hp motors on 10 kW generators.
136,000 BTU's/91,690 BTU's in a gallon of propane = 1.48 gallons per hour.
Travis Creswell