Design Challenge (Was Sunny Island Experience?) [RE-wrenches]

David Katz david at aeesolar.com
Sun Feb 5 10:50:42 PST 2006


<x-flowed>
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Is your computer freezing up or slowing down?
Repair corrupt files and harmful errors - protect your PC
Take a 2-minute PC health check-up at no charge!
http://click.topica.com/caaerelbz8Qcsbz9JC9a/PC Powerscan
-------------------------------------------------------------------

Jeff,
I have a system with two SMA SB1800 inverters feeding a sub panel that 
is also fed by the output of  an outback VFX3524. It works fine, but 
you  have to be careful about preventing the batteries from overcharging 
if your array is producing more than you are using. This could become 
more critical with a larger system, by I see no reason it will not 
work.  You could use the auxiliary relays in the inverters to disconnect 
the AC output of each of the PV inverters at progressively higher 
voltages so they would act like a tapering charge.  Call me if you have 
any questions.

David

David Katz
President, AEE Solar
formerly Alternative Energy Engineering
1155 Redway Drive - Box 339
Redway, CA 95560 USA
Phone (707) 825-1200
Fax (707) 825-1202
email: david at aeesolar.com
web: www.aeesolar.com


Jeff Clearwater wrote:

> Hey Jay,
>
> Thanks for that,  However you said grid-tied version - did you mean 
> the SB or in a grid-tied system?.  This is off-grid.  No utility on 
> the other side of that isolation relay!.  Still work?
>
> Thanks again!
>
> Jeff
>
>
>

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Sign Up for Packet8 and tell your phone company
to VoIP-Off. First Month Free! Then up to 50% off your
phone bill.  Free Equipment! Packet8 1-877-868-1135
http://click.topica.com/caaer6vbz8Qcsbz9JC9f/ TMONE
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



</x-flowed>



More information about the RE-wrenches mailing list