PG&E ends E-7 Time of Use metering [RE-wrenches]
Antony Tersol
atersol at owl.csusm.edu
Fri Apr 28 09:31:42 PDT 2006
<x-flowed>
I was able to find the proposed rate schedule buried in the advice letters
submitted to the CPUC. The attachment is 224 pages. E6 starts on page 48.
http://www.pge.com/nots/rates/tariffs/advice/adviceletters/2810-E-A.pdf
Among the changes:
differential between peak and off-peak reduced from
.20708 under E7 to
.11439 under E6
peak time -
E7 12noon - 6pm
E6 1pm - 7pm
addition of part peak time, which is 10am - 1pm, 7pm - 9pm
Summary of each below.
Regards,
Antony Tersol
Applied Solar Energy
summary of E7: (sorry if the formatting makes it hard to read. original is .pdf)
SCHEDULE E-7—RESIDENTIAL TIME-OF-USE SERVICE
SCHEDULE E-7—RESIDENTIAL TIME-OF-USE SERVICE
TOTAL RATES (as at 1/06)
Total Energy Rates ($ per kWh) PEAK OFF-PEAK
Summer
Baseline Usage $0.29372 $0.08664
101% - 130% of Baseline $0.29372 $0.08664
131% - 200% of Baseline $0.3769 (I) $0.16989 (I)
201% - 300% of Baseline $0.45390 | $0.24682 |
Over 300% of Baseline $0.49422 (I) $0.28714 (I)
Winter
Baseline Usage $0.11472 $0.08966
101% - 130% of Baseline $0.11472 $0.08966
131% - 200% of Baseline $0.19797 (I) $0.17291 (I)
201% - 300% of Baseline $0.27490 | $0.24984 |
Over 300% of Baseline $0.31522 (I) $0.29016 (I)
Total Baseline Credit
($ per kWh of baseline use) $0.01559 $0.01559
One-Time Installation Charge ($ per meter) $277.00
Total Meter Charge Rate ($ per meter per day)
E-7 $0.11532
Rate W $0.03843
Total Minimum Charge Rate ($ per meter per day) $0.14784
TIME PERIODS: PEAK: 12:00 noon to 6:00 p.m. Monday through Friday
OFF-PEAK: All other hours
summary of E6:
Total Energy Rates $ per kWh) PEAK PART-PEAK OFF-PEAK |
Summer |
Baseline Usage $0.20863 $0.11180 $0.09424 |
101% - 130% of Baseline $0.22422 $0.12739 $0.10983 |
131% - 200% of Baseline $0.31414 $0.21731 $0.19975 |
201% - 300% of Baseline $0.39725 $0.30042 $0.28286 |
Over 300% of Baseline $0.44081 $0.34397 $0.32641 |
Winter |
Baseline Usage – $0.12419 $0.10048 |
101% - 130% of Baseline – $0.13978 $0.11607 |
131% - 200% of Baseline – $0.22970 $0.20599 |
201% - 300% of Baseline – $0.31281 $0.28910 |
Over 300% of Baseline – $0.35636 $0.33266 |
|
Total Meter Charge Rate ($ per meter per day) $0.25298
Total Minimum Charge Rate ($ per meter per day) $0.14784
3. TIME PERIODS: Times of the year and times of the day are defined as follows:
Summer (service from May 1 through October 31):
Peak: 1:00 p.m. to 7:00 p.m Monday through Friday
Partial-Peak: 10:00 a.m. to 1:00 p.m.
AND 7:00 p.m. to 9:00 p.m. Monday through Friday
Plus 5:00 p.m. to 8:00 p.m. Saturday and Sunday
Off-Peak: All other times including Holidays.
Winter (service from November 1 through April 30):
Partial-Peak: 5:00 p.m. to 8:00 p.m. Monday through Friday
Off-Peak: All other times including Holidays.
Holidays: “Holidays” for the purposes of this rate schedule are New Year’s
Day, President’s Day, Memorial Day, Independence Day, Labor
Day, Veterans Day, Thanksgiving Day, and Christmas Day. The
dates will be those on which the holidays are legally observed.
orignal message:
------------------------------
Date: Thu, 27 Apr 2006 15:56:58 -0700 (PDT)
From: Jerry Caldwell <solarcowboy at yahoo.com>
Subject: PG&E ends E-7 Time of Use metering
California Wrenches in PG&E territory should be
interested to know that as of May 1, 2006 the utility
will no longer accept applications for the E-7
residential Time of Use metering rate.
They are going to offer a new rate called E-6, which
hasn't been clearly defined to the public as of yet.
It has been hinted at that E-6 will not be as
beneficial to customers. I have a colleague rushing
off to the local office to submit an application and
check as I write this.
If any of you have customers wanting to switch to TOU,
now is the time to act.
Best,
Jerry Caldwell
Berkeley, CA
__________________________________________________
Do You Yahoo!?
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list