Installing higher voltage array grid tie system. Normally we route from fused array combiner to inverter down outside wall to exterior dis-connect (no fuses), then to interior inverter(s). Client's architect vetoed exterior conduit and wants to route through roof and down inside exterior wall to above described exterior dis-connects at ground level.
We have been designing to 2005 code although this county still using older code. New section 690.31 (E) "Where direct-current pv output circuits are run inside a building, they shall be contained in metallic raceways from point of penetration to first accessible dis-connect."
also,
Section 690.14 (C) 5. Grouping. "The pv dis-connecting meansshall be grouped other dis-connecting means....."
Question - Does this require Intermediate Threaded Metal Conduit or is EMT allowed? How about conduit above roof line?
Question - I think inspector may ask us to move the DC array dis-connect from back of house to side where meter base and AC dis-connect are located due to above. Does this mean up to 6 array dis-connects shall be grouped together, or ALL power source dis-connects to house grouped together?
Thanks,
Jeff Yago
_____________________________________________________________
Netscape. Just the Net You Need.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & how to change your email address: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list